DIFFERERTIAL PRESSURE VALVE
mike terry
mike terry Member Posts: 33
WOULD ANYONE KNOW WHERE I COULD PURCHASE A LARGE VALVE OF THIS TYPE?
  • Paul Rohrs_2
    Paul Rohrs_2 Member Posts: 171
    Bypass?....
    Are you looking for a pressure differential bypass valve? Wirsbo has them available in 34" and 1". What flow rate are you looking for?
    PR
  • BillW@honeywell
    BillW@honeywell Member Posts: 1,099
    Differential Pressure Regulator(Valve?)
    If a valve that maintains a constant differential between the supply & return sides of a hydronic system is what you're looking for, try the Honeywell D146. It is available in two sizes, D146M1032 3/4" for 18 gpm or D146M1040 1&1/4" for 50 gpm. Contact any Honeywell distributor, or call 401 738 4290, choose option 6.
  • Joe Lambert
    Joe Lambert Member Posts: 18
    Larger Yet
    Spence makes pilot operated differential pressure valves up to 6", this is not for home use, too big.
    Look at: http://www.spenceengineering.com/Handbook/n_pilot.pdf
  • Art Pittaway
    Art Pittaway Member Posts: 230
    What's it for?
    Cal-Val (Clayton Valve, Newport Beach, Ca.,) makes them thru 24" I believe. But, they are not for hot water service, max temp. 180*f. Application makes a huge difference to the valve and mfg. co you go to. Also, the little honeywell and others like it are simple spring operated units, and they work fine. Bigger valves like Cla-Val are pilot operated. Installed correctly they will hold your pressures dead nuts on what you want.
    Best luck, Art
  • mike terry
    to all that responded.this is a bypass for a chilled water system.bypassing when modulating valve closes.just need to give the water some place to go.
  • Jerry Boulanger
    Jerry Boulanger Member Posts: 31
    Griswold Controls
    makes a diaphragm valve up to 3" for this purpose as well. They are in Irvine, CA.