Anticipator settings - 24 volt system

Options
Charlie_3
Charlie_3 Member Posts: 3
I have a 2-zone hot water baseboard system in a rental property. The thermostats are Honeywell round type, the thermostat cicuit is 24-volt. The tenant told me that the heat doesn't come on at all unless she turns it up all the way (10-15 degrees above the room temp.). The plumber who installed the system a number of years ago ('89) says the anticipator should be at minimum setting for this system. So I set the anticipator at minimum (it was at 0.3 before) and turned the dial up. The mercury made contact about 2 degrees above the room temp on the thermometer. Then I watched as the thermostat shut itself off again, apparently as the anticipator heated up. Once this happened, I had to turn the thermostat to 85 to get the mercury to fall back again. When I saw a wisp of smoke near the anticipator, I set the settings back where I had them!
Can someone explain the theory behind anticipators? I am having trouble finding good information. Or maybe there is something else I am overlooking and it's not the anticipator at all. Any input would be appreciated.
Thanks.

Comments

  • [Deleted User]
    Options
    Oh oh....

    Sounds like you might have let the smoke out of the anticipator... You may need a new thermostat.

    As the name implies, the anticipator "anticipates" the room being satisfied before it is actually satisfied.

    IMHO, it is a throw back to the old days of inefficient heating systems whereby there was a WHOLE bunch of heat left in the heating system to still come into the house after the thermostat was satisfied. Hence, the anticipator shut the heating system down early knowing that there are a whole bunch of btus that hasn't even made it into the room yet, so in anticipation of this, it shuts down early.

    Industry practice is to set the anticipator for the actual amp draw of the device it is controlling. Unfortunately, there are some devices out there (older Taco heat motor types of operators) that have a REALLY big amp draw and will cause the scenario you just explained. Although it's probably a poor practice, I usually turn these anticipators completely up to eliminate their function, and I've never had anyone complain of excessivley warm environments.

    Just my opinion though...

    ME
  • heatboy
    heatboy Member Posts: 1,468
    Options
    Taco Zone Valves?

    These are famous for letting the smoke out of anticipator circuits when installed by..........non-technician types.

    hb

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"

    There was an error rendering this rich post.

  • Larry_7
    Larry_7 Member Posts: 86
    Options
    Maybe Too Late

    10-15* sound a little far out of whack. The Round is able to be re-calibrated using a special skinny wrench after making sure the stat is level and secure. Needs to be done before smoking the anticipator, though. I have made smoke a coupla times and still saved the sucker by shutting it off in time. There is usually very little time to take remedial action once the first wisp is observed. Ohhh sh.. If you complete the sentence, it's too late.

    Larry
  • D lux_2
    D lux_2 Member Posts: 230
    Options
    IS it level?

    I have found the subbase out of level causeing prob.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"