Please Help

Tom M.
Tom M. Member Posts: 237
I posted about this last week and was referred to Dan's book E.D.R. I have ordered the book and intend to keep it for future use but it has not yet arrived. The customer is pressuring me for time and I don't want to give him a price without properly sizing the boiler. I would appreciate it if someone could send this info by email to scoopdaddy11@yahoo.com.

The original post was:

http://forums.invision.net/Search_Results.cfm?CFApp=2#Message38716

Thanks in advance for any help. Sorry about the frantic post. I've got the day off and my family is waiting for me. Tom M.

Comments

  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Can't help with convector

    but the indirect "pin" radiator is most likely 20 sq.ft. EDR per section.

    Your height measurement (18") doesn't seem to fit any listed exactly, BUT if it is a "Gold Pin" and you measured the end with the connecting tubes, this part is bulged out a bit and the 15½ nominal size would likely measure about 18"

    Don't see ANY listed above 20 sq.ft./section.
  • Steamhead
    Steamhead Member Posts: 17,387
    Tom, if you're not sure

    what they are, how about posting a picture here to help us identify them? BTW, I tried to access the earlier post but it's a goner.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Tom M.
    Tom M. Member Posts: 237
    Thanks, Steamhead.

    I don't have picture capability but here is a description:

    They were sheet metal convectors with cast iron heat exchangers in them. They were 14 section on 2" centers. They slanted from front to back and the fins on the sections slanted up toward the front to draw the airflow through the sections. Both were built into the walls, one had a cabinet 23"H X 33"L the other was 21"H X 33"L. Both were approx. 7 1/2" deep.

    Thanks again.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601


    Retired and loving it.
  • kevin
    kevin Member Posts: 420
    I'm looking...

    in the Burnham heating helper...going by the 6.5" deep CI convector 23.5" X 32" I read approx 22.6 sq. ft of rad. X 240/sq. ft. about 5424btu.
    The other one is about 25.2 sq.ft. approx
    It's not exact but in the ballpark...kpc
  • Tom M.
    Tom M. Member Posts: 237
    Thank You All

    These numbers should be close enough that I can use the correct boiler size.