CT2700
BillW@honeywell
Member Posts: 1,099
The resistor is a 7.87K ohm type. It's used with power stealing stats on TACO green zone valves, on terminals 1&2, or on the Honeywell R8184G oil primary between the lower T & lower F terminals. There is a Honeywell part number for it, 4074EYC. If you like to upgrade to a trade model, use the T8002C1000. That is battery powered digital programmable, compatible with steam, hydronic or forced air.Since I have no information on the retail product, I can't be certain that the resistor will solve your problem. Any Honeywell distributor will have the T8002C1000, or can order it. Take care!
0
Comments
-
Honeywell CT2700
Installed two W/M CGs using CT2700 T-stats.
The T-stats lose their display when the boilers are on.
Display returns and program is normal when boiler shuts down. Any suggestions. Anyone have the link to honeywells tech site?
Thanks0 -
CT2700
Those stats are retail models sold only through Home Depot or Lowes or other box stores. I do not have any information on the retail lines, but the symptoms you describe are consistent with power stealing thermostats blanking out on startup, due to losing power. Trade model stats come with a resistor to add into the system, but I doubt that the retail models include them, and they are not available at the box store. You best solution would be to use a battery powered thermostat, or call a professional, using the "find a contractor" feature above.0 -
Thanks Bill. VERY INTERESTING.The homeowner provided the t-stats because the wife liked the design.
Do you know the resistor size? Or should I swap to a couple of T8400's0 -
losing display
another option we have done many times is install a isolation relay on equipment, then you wont lose feed back power which these stats rely on. Go from transformer on equip and run common to one side of coil and R off transformer up through thermostat and to other side of coil. then use the contacts on relay to switch T&T on unit. This will take care of power loss to thermostat.0 -
I don't know if this is too little, too late,
but if it helps you, here is a link to installation instructions for the CT2700 T-stats. It appears to be the same as the Trade version T8700 series digital round t-stat, which I believe has been discontinued, but Bill W. can feel free to correct me on that.
http://hbctechlit.honeywell.com/techlit/PDF/69-0000s/69-1085.pdf
0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements