steam baseboard

paul_14
paul_14 Member Posts: 16
i have a 15'x25' room with 3 outside walls and 8'ceilings i was going to run 16' of steam baseboard off a 1" line one pipe steam with min. pitch and a heal tee before the rad valve with a self bleeder coming out of the top and a good air vent down the end.could this work without having problems

Comments

  • On one pipe steam

    an inch and a quarter radiator valve will pass about 13000 BTUH before you get water weight gain in the baseboard (it won't drain back) One inch isn't on the chart for one pipe.

    Noel
  • Ben_3
    Ben_3 Member Posts: 71
    Baseboard

    No it won't work, it's difficult to make any baseboard work with one-pipe, but it can be done, just don't counterflow it and drop the return back wet and make sure you pitch it correctly so it will drain without hammer, Do not use a trap, if you do it will never work, this is one of those times you hook up two pipes to a one pipe sysem and you need the steam to help you get the condensate back to the boiler. Put the vent at the end of the BB before you drop the return back
  • Steamhead
    Steamhead Member Posts: 17,387
    This is covered

    in Dan's book "The Lost Art of Steam Heating". Basically, Noel and Paul are right- there is no way baseboard can work when piped like a one-pipe radiator. You can hook it up two-pipe in a one-pipe system, and the book shows you how.

    If you don't already have it, order your copy on the books and More page of this site.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • paul_14
    paul_14 Member Posts: 16
    steam

    ok thats what im goin to do one more thing how do you figure out how much steam baseboard i would need for a room
  • Do a heat loss survey

    but do all of the rooms, then see how much radiation is in each room. If balance is going to be achieved, you need to have the new piece be oversized the same per cent as the rest of the radiation is.

    http://www.slantfin.com/hydronic/index.html