steam baseboard
paul_14
Member Posts: 16
i have a 15'x25' room with 3 outside walls and 8'ceilings i was going to run 16' of steam baseboard off a 1" line one pipe steam with min. pitch and a heal tee before the rad valve with a self bleeder coming out of the top and a good air vent down the end.could this work without having problems
0
Comments
-
On one pipe steam
an inch and a quarter radiator valve will pass about 13000 BTUH before you get water weight gain in the baseboard (it won't drain back) One inch isn't on the chart for one pipe.
Noel0 -
Baseboard
No it won't work, it's difficult to make any baseboard work with one-pipe, but it can be done, just don't counterflow it and drop the return back wet and make sure you pitch it correctly so it will drain without hammer, Do not use a trap, if you do it will never work, this is one of those times you hook up two pipes to a one pipe sysem and you need the steam to help you get the condensate back to the boiler. Put the vent at the end of the BB before you drop the return back0 -
This is covered
in Dan's book "The Lost Art of Steam Heating". Basically, Noel and Paul are right- there is no way baseboard can work when piped like a one-pipe radiator. You can hook it up two-pipe in a one-pipe system, and the book shows you how.
If you don't already have it, order your copy on the books and More page of this site.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
steam
ok thats what im goin to do one more thing how do you figure out how much steam baseboard i would need for a room0 -
Do a heat loss survey
but do all of the rooms, then see how much radiation is in each room. If balance is going to be achieved, you need to have the new piece be oversized the same per cent as the rest of the radiation is.
http://www.slantfin.com/hydronic/index.html
Noel0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements