steam trap bypass
john_24
Member Posts: 23
I am sure That I havnt seen as many steam jobs as most of the experts on here but I have seen my share of them. Today I saw something new and was hoping for an explanation. I went to a job for a noise call and found that a ton water hammer was the culprit. After going over the system I found that someone had piped a bypass to one of the main steam traps in the basement. I shut the valve eliminating the bypass and the noise went away. I cant think of any reason why you would try to bypass a trap but then again I dont know it all. any ideas?
thanks in advance
John R
thanks in advance
John R
0
Comments
-
I've seen that.
> I am sure That I havnt seen as many steam jobs
> as most of the experts on here but I have seen my
> share of them. Today I saw something new and was
> hoping for an explanation. I went to a job for a
> noise call and found that a ton water hammer was
> the culprit. After going over the system I found
> that someone had piped a bypass to one of the
> main steam traps in the basement. I shut the
> valve eliminating the bypass and the noise went
> away. I cant think of any reason why you would
> try to bypass a trap but then again I dont know
> it all. any ideas? thanks in advance John R
0 -
I've seen that.
Three bypasses in one building. Way out at the ends of the mains. I never figured out why they were there. 3/4" with a plug cock in them, around an F&T trap, in each case.
It was a 1911 building, with a Vari-Vac system.
I closed them.
Noel0 -
closing solved the problem here too. I just dont like not knowing why its there. but guess i cant know it all
thanks
John R0 -
The REAL kick in the pants is
Why were they open, in both cases?
Noel0 -
Those bypasses
were put there so if the F&T traps failed, you could work on them without shutting down the system. You'd throttle the bypass so it would let the air and water pass but not let too much steam thru.
Why were they open? Probably someone didn't know what they were doing.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Manual startup
on large mains that are starting from cold will produce a lot of condensate, initial air and non-condensibles. The bypass allows the mains to drain and vent freely until they get warm, then are closed. Some large high pressure mains have two traps set at different pressures. When the main is starting a 30# trap and a 100# trap discharge the large flow. As the pressure builds the 30# trap is "locked closed" by the pressure, leaving the proper main drip trap to deal with everyday loads.
Art0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements