Adding Fin baseboard with a cast iron system?
Boilerpro_3
Member Posts: 1,231
To help reduce the pressure drop problem described above you could try commerical or light commerical baseboard that has a large pipe diameter....1 inch or 1 1/4 inch. Also since cast iron radiators hold heat longer than light weight baseboard, you will want to keep the water circulating constantly so the stored heat in the radiators can be transfered to the baseboard between burner cycles. Soooo much to watch out for!
Boilerpro
Boilerpro
0
Comments
-
Adding Fin baseboard with a cast iron system?
Can I add fin baseboard to a single pipe monoflo system. The rest of the radiators on that zone are all cast iron? Thanks0 -
Monoflow baseboard
Anthony be careful here. You can add the baseboard as long as the pressure drop through it is equal to the radiation that you are removing. If the baseboard and it's piping is more restritive the water won't want to divert that way and will leave you with a cold baseboard. In short, small lengths work but longer lengths don't and typically you will need alot of b.b. to equal the output of that old radiator. One way around this is sometimes on smaller zones if you really need all that b.b. you can run it as part of the main but this to can be tricky. Hope this helps, good luck0 -
Why not
use cast-iron baseboard, as made by Burnham, Slant/Fin or Weil-McLain? It will hold its heat just like those cast-iron radiators do, and I think its internal resistance is lower too.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The output from the two
are actually pretty close. The problem is the flywheel effect from the cast iron holding the heat better than the bang/bang, off/on, output from the copper finned tubing.
As a rule I never combine the two in a zone. Yes it can been done but there allways seems to be a balance issuie.
Scott
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements