Can I cap a MONOFLO TEE?

anthony_7
anthony_7 Member Posts: 72
I have to remove a cast iron radiator from my single pipe system. I know I can cap the regular Tee on that radiator.

My question is can I do the same for the monoflo tee or do I have to completely cut out the monoflo tee and put in a coupling. Will it screw up the rest of my system if I do not totally get rid of the Monoflo Tee. Thanks

Comments

  • Ben_3
    Ben_3 Member Posts: 71
    Monoflow

    Anthony, Instead of capping the regular tee and removing the diverter tee just connect the two. If you cap the monoflow tee you give the water in the system only one option to go instead of two like it had before. That one path also happens to have a large restriction in it, the one that was once used to divert flow to the radiator. By connecting the two tees the water still can split and rejoin in the regular tee at full flow, everybody wins.
  • Fran
    Fran Member Posts: 4
    momoflo tee

    you must replace the tee with a coupling or you will reduce the amount of flow in your main.
  • Jeff_9
    Jeff_9 Member Posts: 7
    Monoflow tees

    In hot tech topics it will explain all you need to know about monoflow tee's This is a great resource for (thanks Dan)


    Jeff
  • kevin
    kevin Member Posts: 420
    i aggree...

    with ben. It also allows you to add the rad or kick in later.kpc
  • MURPH'
    MURPH' Member Posts: 88
    Maybe

    throw in a couple valves to reconnect later??