B&G ZONE VALVES

Paul_15
Paul_15 Member Posts: 1
I have 3/4" B&G valves installed on a hydronic baseboard job. The Bonnet and interals are always failing. The system has recently had "No-Burst" added to the system. Can this glycol be destroying the internals of the valve?

Or is this just a Piece of Junk valve?

Thanks

Comments

  • hot_rod
    hot_rod Member Posts: 23,388
    Check the fluid

    while it's not my favorite valve, frequent failures are probably not the fault of the valve. My guess is the ph has dropped and the fluid is attacking the seals.

    Buy a ph tester, or take a sample to a chemical supplier familiar with glycol testing. Most glycol manufactures will also accept a "mailed in" sample for a complete check.


    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • John Abbott
    John Abbott Member Posts: 358
    B&G Zone valves

    > I have 3/4" B&G valves installed on a hydronic

    > baseboard job. The Bonnet and interals are always

    > failing. The system has recently had "No-Burst"

    > added to the system. Can this glycol be

    > destroying the internals of the valve?

    >

    > Or is

    > this just a Piece of Junk valve?

    >

    > Thanks


  • John Abbott
    John Abbott Member Posts: 358
    B&G zone valves

    Unless they have changed their design they were in my experience just about total junk with or without propylene glcol. The most troublesome by far that I ever used.

    John