B&G ZONE VALVES
Paul_15
Member Posts: 1
I have 3/4" B&G valves installed on a hydronic baseboard job. The Bonnet and interals are always failing. The system has recently had "No-Burst" added to the system. Can this glycol be destroying the internals of the valve?
Or is this just a Piece of Junk valve?
Thanks
Or is this just a Piece of Junk valve?
Thanks
0
Comments
-
Check the fluid
while it's not my favorite valve, frequent failures are probably not the fault of the valve. My guess is the ph has dropped and the fluid is attacking the seals.
Buy a ph tester, or take a sample to a chemical supplier familiar with glycol testing. Most glycol manufactures will also accept a "mailed in" sample for a complete check.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
B&G Zone valves
> I have 3/4" B&G valves installed on a hydronic
> baseboard job. The Bonnet and interals are always
> failing. The system has recently had "No-Burst"
> added to the system. Can this glycol be
> destroying the internals of the valve?
>
> Or is
> this just a Piece of Junk valve?
>
> Thanks
0 -
B&G zone valves
Unless they have changed their design they were in my experience just about total junk with or without propylene glcol. The most troublesome by far that I ever used.
John0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements