Underground heating pipe questions
George Peteya
Member Posts: 34
Mark, I sold Ecoflex for a while (or tried to, it was way pricey). We were told to never run it in a straight line, but to "snake it," for the very reason you describe.
0
Comments
-
Underground heating pipes
Job opportunity to replace existing copper L hard pipe which is underground. 2-2" Copper pipes are used for heating. 2-1 1/4 pipes are used for domestic water (hot and cold). Heating water temperature is 200 degrees. Existing pipes had no insulation, just laid in screenings. In this same trench is an electric conduit. Boiler building feeds apartments 100 feet underground. What kind of pipe would you suggest? Thanks in advance~Randy0 -
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The Dead Men
used to build conduits to run these pipes in. They insulated the pipes and installed drains so the conduits would not fill with water and saturate the insulation, which destroyed its effectiveness. Any kind of pipe should work OK in this setup.
I think you can get conduits pre-cast now. Sure, it would cost more to install, but they wouldn't lose nearly as much heat from the pipes as before. This would reduce the system's operating cost.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
A couple more ideas
This EcoFlex product is available in various sizes for hot and cold applications. A bit spendy but quick jointless product in a well insulated waterproof jacket. I'm not sure who is currently handleing it. Try Wirsbo or Rehau.
I have also used a product calles insulseal. It's is commonly used with outdoor wood fired heaters. It is an insulated pvc tube that you slide the copper or pex lines inside. A condiut really. Allows you to remove or replace the pipes also. www.insulseal.com
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Perma-pipe/Ricwil
They have a web site and have made direct bury insulated pipe of all kinds for a long time. Pretty good people to work with. We buried the chilled water pipe on a school project, contractor had no problems. Some water pipe is solid foam fill in PVC jacket, you sweat the copper and test the joints then foam and seal with shrink tube. Ever see a piece of 10" shrink tube? Ships from Chicago area I think.
Art0 -
Don't forget...
if you use PEX it has a VERY high coefficients of expansion. 1.1" per hundred feet per 10 degrees F chnage in temperature. Too long of a run and you could have pipes coming out of the ground the first time you heat it up to 180 degrees F.
ME0 -
Insulated pex
Uponor ( Wirsbo Parent Co.) markets Ecoflex. Rehau sells Insulpex. Ecoflex has multiple layers of foam insulation in an outer plastic conduit. Insulpex is pexA foamed in in a plastic conduit. Similar but different. take your pick. I think its phillips or hexhead screw which do you prefer?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements