Glycol or Inhibitors?
Drew_2
Member Posts: 158
John,
Before you add anything to the water, take a look at this
article, "Water Samples Needed for Warranty Claims"http://www.heatlink.com/pdf/mar2001.pdf. It's important that the additive put into a system have data to back-up the claims that are made or a long history of use
with good results. Most customers expect the system to work
well thru the first decade of use with very few problems.
Drew
Before you add anything to the water, take a look at this
article, "Water Samples Needed for Warranty Claims"http://www.heatlink.com/pdf/mar2001.pdf. It's important that the additive put into a system have data to back-up the claims that are made or a long history of use
with good results. Most customers expect the system to work
well thru the first decade of use with very few problems.
Drew
0
Comments
-
System treatment
looked at a job tonight that is going to need a corrosion inhibitor. Staple-up system with a LOT of non-barrier tubing. System content could be as high as 75 - 100 gallons (rough estimate). Is there a corrosion inhibitor that can be used that would be less problematic than glycol? (heat transfer, expansion rate, viscosity) Whould it be easier to obtain/maintain glycol? (freeze protection not really an issue) What about cost? I've never used an inhibitor by itself.
John Taylor
Custom Climate Systems, Inc.
Whitmore Lake, Michigan0 -
I would use both
& do quite often to extend life of system when oxygen is an issue. I use the Heat link moly inhibitor and polypropylene glycol most times - but have used Fernox with excellent success too. The client will have to buy into annual pH and glycol tests as well.0 -
How about.........
isolating the tube with a heat exchanger?If glycol is needed for freeze protection you can still add antifreeze.But the HX will prevent 02 diffusion to your equipment.
cheese0 -
What type of tube?
I'd stay away from glycol, unless freeze protection is needed. Expensive, messy, changes pump spec, etc, etc.
Of all the various brands of inhibitors I have used, so far the best is this Rhomar product. It's the only product that I know of that was blended specfically for modern hydronic applications. Blended to be used with iron, steel, copper, stainless, yellow metals (brass etc) and aluminum.
They also have a cleaner that I highly recommend you use first to flush and condition the system. 800-543-5975
hot rod
heatboy
"Expert in Silent Warmth" Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks Hot Rod
Was hoping someone might be able to make a recommendation of a product they had some experience with. Cleaner sounds like a good idea too. I know hx isolation would be best but the cost of replacing all the iron components would be prohibitive. The designer believes neither is required so I kind of sound like chicken little.
Thanks again.
John Taylor
Custom Climate Systems, Inc.
Whitmore Lake, Michigan0 -
Glad to see Heatlink
take a position on water quality. Will they test water and treatments as a service to their customers?
Water chemestry and water treatment, as you know, is a very complex science. Other tube manufactures have walked this road with mixed results. You may recall others that sold cleaners and conditioners as part of the package.
I have done a lot of research in this area. Talked to a handful of chemical and heat transfer chemical experts. Designing a cleaner and inhibitor to work with all the modern hydronic components, buffer both ends of the ph range, provide O2 scavangers, film providers, disperents, and be enviromently friendly is a very tall order.
Add to this the unknow quality of water that will be blended in, shelf life, enviromental concerns, etc and you have a real challange.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
A non-oxygen barrier staple up tubing system?
John T:
Did you say you have a non-oxygen barrier staple-up tubing system with ferrous components, no water treatment, no isolating heat exchanger, and the designer doesn't think there is a problem?
You're not Chicken Little. You have every right to be concerned.
Senior Designer/Trainer
Precision Hydronics Corporation
www.precisionhydronics.com0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements