80PLUS furnace cutting out
John Mills_3
Member Posts: 221
Floyd may be right. That's the most common time when we find rollout problems on inshot burners. Venting issues can if the flue draft is borderline. Usually they'll trip a pressure switch but not always. But scope out that heat exchanger really good. Worst place for cracks is right where the fire shoots in. Also, check for popped crimp rings holding the sections together.
0
Comments
-
80PLUS furnace cutting out
Hello all,
I visited a Tempstar fan assisted nat gas furnace, it has locked out several times at the roll out switch at the burner area. This is also a new switch... the old one couldn't be reset.
What are some common reasons for this? It has a modern metal chimney liner, could it be a venting issue? If it was a venting issue, why wouldn't the fan limit kick off the burners? There was a bunch of dust building up as well, could a gooked up HX be a problem? I'm leaning towards the latter.
Thanks,
Gary
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Heat exchanger....
is cracked....indoor fan comes on and blows the flame out the wrong way....:-)0 -
Check for enough make-up air, too
See if it vents properly with all doors closed, dryer running, any exhaust fans running, and even ask if you suspect a fireplace running might be pulling air down the venting system.
Check to see if the burner is overfired, too.
Noel0 -
air
Noel,
Forgive the dumb question, but why would make up air be an issue? That is, the rollout problem. Unless the basment is negative, I'm not sure how this applies.
Gary
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements