referencing boilerpro's orifice question furthur down

the orifice size to edr square feet for a given vapor pressure? i was thinking these could probably be made with copper shim stock if the measurements for the holes in the radiator valves orifice plate were known.

Comments

  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    I think I know someone that does

    and I may have it here somewhere. Making them might be the easiest answer instead of buying,like you were saying.

    Boilerpro
  • cool, if you can dig it up somewhere

    please post.
  • Ben_3
    Ben_3 Member Posts: 71
    orfices

    Most of the books I have state that with vapor {.5 psig @ the radaitor @ 190 will be 185 btuh/sq. ft. edr for the rad.size} you should only allow 80% of what the rad. can condense i.e. 100 edr should only allow 80 edr into rad to ensure no steam in return. you could even size the orifice to the rooms heat loss as a % of the edr. Dan's book lost art 2 has an old trane heatloss for vapor and vapor/vac. systems complete w/ pipe sizing it's great I have used metal and drilled a hole to size and put in union so they can still throtle valve down like a true vapor. Good Luck
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    Will be working on it , but off to Chicago first

    And the person who I believe has just left for Vegas....It will probably be few weeks before I find it....Maybe I'll find it in Chicago.


    Boilerpro