Munchkin blower failure

Bill_15
Bill_15 Member Posts: 1
We have had several blower failures on munchkin 199 boilers.
All have been a structural failure of the plastic fan attachment to the motor shaft. Has happened to boilers with minimal vent and with considerable vent runs. Anyone else seen this problem?

Comments

  • Troy_3
    Troy_3 Member Posts: 479
    Blower failures

    The factory is aware of the component failures. My understanding is they are working with the blower company on a beefed up blower. To be out soon. We are not seeing them fail on boilers with the 925 control. The control seems to ramp up slower. Less torque- less stress on the impeller.
  • James_2
    James_2 Member Posts: 24
    Munchkin Blowers

    The new blowers are available. Our rep has updated all his stock. The new blowers include a new wire harness that will eliminate improper installation. Might want to order a new fan outlet gasket if you have an older unit. Request a new unit drop shipped from the factory. Then you will get the new version.
  • munchkin-man
    munchkin-man Member Posts: 247
    new syle blower motors are in and available for the 199M