steam in dry return

steve_6
steve_6 Member Posts: 243
worked on a steam job today. while replacing a return pipe with a big belly in it we noticed steam coming from it after a while. we found a few bad radiator traps that we'll replace tomorrow.my question is should there ever be any steam in a dry return?

Comments

  • Steamhead
    Steamhead Member Posts: 17,230
    If the system has traps

    there should never be steam in the dry return. What kind of Vapor system is it?

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    Don't forget alternating recievers...

    they can let steam into the return. I was out on a system friday and saturday with a Sterling unit in, guess where, Sterling Ill.... however no relation. My first one in real life...system's a mess, but hopefully will be saved. Boiler twice as big as necessary running 5 to 8 lbs, rad vents on some of the rads, a little hofman 75 for the main system vent. Hope to get rid of the rad traps and put in orifice plates in the valves. We'll see.

    Boilerpro
  • steve_6
    steve_6 Member Posts: 243
    steam system

    I don't think this system was a particular brand . Regular steam valves and hoffman style steam traps on the radiators. They also used radiator traps to drip the mains into the dry return. System was hacked up. Air vents on about half the radiators, and a boiler feed pump installed on the return. Homeowner states that the heating contractor who installed the previous boiler, a Burnham that only lasted 15 years, had worked on the system for approximately 2 straight months after his install. He added the radiator vents and the boiler feed pump. We installed a new dunkirk sized to the radiation with the proper near boiler piping and found a few problems we listed on the previous posting.
  • steve_6
    steve_6 Member Posts: 243
    steam system