Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
SLANT FIN TUBING
Bill Riordan_3
Member Posts: 31
Does anyone know if Slantfin Terra-Therma 1/2 PEX tubing can be connected to Wirsbo manifolds using Wirsbo compression fittings? Thanks in advance.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=274&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=274&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
Slant/Fin Tubing
If the Wirsbo manifold compression fitting has a split ring, it should work fine. Any pex A, B, or C tube that meets the ASTM F876/877 standards should be interchangeable ... I've used Slant/Fin manifolds, both modular and copper (Dahl valves) with Wirsbo, RTI, HeatLink ... you get the idea.0 -
Thanks
Thanks, just wanted a second opinion.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements