PRESSURE TOO HIGH!?

adambuild
adambuild Member Posts: 414
We have a client with a residential steam boiler that is producing steam to the point where the radiator valves are hissing. I set the Pressurettrol to .5# and cleaned the pigtail but the gauge is still hitting about 3#!? Could it be anything other than a bad Pressuretrol?

Comments

  • b
    b Member Posts: 1
    b

    b
  • Steamhead
    Steamhead Member Posts: 17,396
    Does the Pressuretrol

    actually stop the burner at 3 pounds? If so, either the Pressuretrol or the gauge is not accurate. If not, the Pressuretrol is probably bad but it could also be a wiring problem.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Bob Cat_3
    Bob Cat_3 Member Posts: 8
    Main Vent

    If the guage is bad and the pressuretrol is ok, I would check the main vent. It lets most of the air out so if its not working then the radiator valves have to do its job.You know what happens when you have to do some one elses job don't you? most of us Hiss and moan!

    good luck
  • Arthur
    Arthur Member Posts: 216
    Pressure too high

    Hi,
    Is the pressuretrol set to the pigtail in the correct orientation so that the pigtail under pressure and heat hasn't tilted the pressuretrol and upset the reading?
  • Ben_3
    Ben_3 Member Posts: 71


    Your pressuretrol is doing you a favor by shutting off. Crank that pressure down. Why do you need 5#. Residential systems don't need more than 2psi. Set that control to cut off a 2psi and cut on at 0.5psi. Afterall low pressure steam will not only move faster it will also take less time to make and won't drive the water back up the returns. Those dead men that installed that system never intended it to be run at more than 2psi, after all coal was expensive.