c.i. baseboard
rich_9
Member Posts: 1
can anyone tell me how much burnham 9a baseboard i can run off of 3/4 copper tubing. how many b.t.u per ft thanks rich
0
Comments
-
baseray?
appx 500 btus per ft @ 180. I would venture to say appx 50 ft of baseray on 3/4. All based upon flow rates.