Old base board
Jon S.
Member Posts: 43
Im going to be replacing a section of old cast baseboard. Its attached to a mono flow system. The tapping on the tees for the baseboard is ½ inch. Can I use ¾ inch fin baseboard with a reducer, or will that cause flow problems?
Thanks,
Jon S.
Thanks,
Jon S.
0
Comments
-
Measurement
Jon , how much is * ?0 -
sorry
It must not be showing up as a fraction, The tees are 1/2 inch and i want to use 3/4 inch.0 -
Monoflow
No flow problem with 1/2" risers feeding 3/4" baseboard. But most monoflow-flow problems are the cause of improper spaced tees, lack of a second veturi and air traps.....0