Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Old base board
Jon S.
Member Posts: 43
Im going to be replacing a section of old cast baseboard. Its attached to a mono flow system. The tapping on the tees for the baseboard is ½ inch. Can I use ¾ inch fin baseboard with a reducer, or will that cause flow problems?
Thanks,
Jon S.
Thanks,
Jon S.
0
Comments
-
Measurement
Jon , how much is * ?0 -
sorry
It must not be showing up as a fraction, The tees are 1/2 inch and i want to use 3/4 inch.0 -
Monoflow
No flow problem with 1/2" risers feeding 3/4" baseboard. But most monoflow-flow problems are the cause of improper spaced tees, lack of a second veturi and air traps.....0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements