High temp Hot water

Jim_47
Jim_47 Member Posts: 244
Hello, here I am with another need of the intense inteligence of the members of the wall community.
I am covering maintenance for an industrial application. They buy hot water from a central hot water supply boiler plant. Here is my question:
The water is 375 degrees F at 275psi. There is a flow indicator on the main line coming into the boiler room that indicates 245gpm flow. The return water is varying from 230degrees to 275 degrees F. So I am seeing a temperature drop of approximately 100 - 140 degrees F. Is there anyone here that can help me determine the BTU consumption of this boiler room? Or show me to a source that I could go to find the formula(s) needed for this calculation?
AS always thanks
BTW lots of "dead man" sized pipes in this boiler room.

Comments

  • the formula comes from this one...

    BTUH / (8.3 x 60 x TD) = GPM

    flipped around, I think it reads

    BTUH = 8.3 x 60 x TD x GPM

    BTUH = 498 x 100 x 245
    to 498 x 140 x 245

    or 12,201,000 to 17,081,400 BTUH

    Sound right?

    Noel