Need to replace my WM MGB-6 (cracked casting)

My WM MGB-6 steam boiler developed a crack in the boiler casting and I am humidifying my neighborhood via the chimney! The leak is not bad enough to cripple the house heating; it can keep up down to zero Fahrenheit (tested in action).

My heating contractor wants to replace it. Its specs are 850 MBH in, 680 MBH out, 2125 ft^2 steam.

What are your suggestions for a replacement?

Many thanks in advance.

Comments

  • steve_6
    steve_6 Member Posts: 243
    boiler

    How old is your boiler?
  • Earthfire
    Earthfire Member Posts: 543
    steamreplacement

    have a correctly sized boiler installed by a knowledgable contractor who sizes it to your connected load not the building manual J load, or worse"that's whats here already". Also it should be installed with applicable codes and manufacturers instructions as the MINIMUM acceptable standard.The best boiler is one that is properly installed & serviced,& supported by a wholesaler that will be there to assist the contractor with parts and any possible service issues.
  • Ray M_2
    Ray M_2 Member Posts: 64
    Crack in casting

    You could replace the section if the boiler is in otherwise good condition.A measurement of the rads are needed and piping pick up to size a new boiler.
    lol Ray M

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Mike Valentine
    Mike Valentine Member Posts: 6
    How old is it?

    I think it's only 25 to 30 years old.
  • Mike Valentine
    Mike Valentine Member Posts: 6
    Parts supply?

    The MGB-6 is no longer listed as a current item on the WM web site. Are spares generally available for out of production designs?
  • Boilerpro_2
    Boilerpro_2 Member Posts: 89
    Follow Earthfire's Advice

    Just was out recently on another Weil Mc Lain LGB about 750,000 input. Besides a welded header with no offsets and no Hartford Loop (Geee, guess what its leaking!), my immediate reaction was that the boiler was way too big. I disconnected the high fire wire on the gas valve and ran it on low fire only (50% fire). When I left the site it had already built a pound of pressure. Another cracked Weil MGB steamer I replaced about 4 years ago...my first steam boiler replacement...was 650,000 imput and I replaced it with a 200,000 input steamer. Fuel usage dropped about 40% and the comfort improved beyond belief. Definitely get it sized right..too big or too small will cost you a fortune in fuel and comfort.

    Boilerpro
  • Steamhead
    Steamhead Member Posts: 17,357
    Perhaps just as important, Mike

    is trying to ascertain why it cracked.

    Was the low-water cutoff working?

    Was the piping around the boiler done according to W-M's specs?

    Was the boiler sized properly to the building's radiation?

    Was the boiler firing at the proper rate?

    Are all the system's air vents properly sized and working?

    Are the return lines flowing freely?

    Is the pressure set no higher than the system was designed for?

    Is the water feed line piped into the wet return, so cold water will not shock the boiler?

    Any time I assess a system with a cracked boiler, I look for things that could cause the crack. Often I find more than one of the above. I recently looked at a Hoffman Vapor system with a Columbia boiler that had cracked for the second time. The first time someone replaced the bad section and hoped for the best. This time it gets done right!

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Mike Reavis_2
    Mike Reavis_2 Member Posts: 307
    MGB Sections and repair kits

    are listed in the w/m discontinued boiler parts catalog. Your contractor can see his distributor for these parts if this is the way you would like to go. Mike
  • Hope you don't need

    the right end section. I got the last one in November. The MGB was discontinued in the late 70's - early 80's.
    Wasn't a real good steam boiler. Narrow sections, low water content, & a whole lot of fire.

    Unless you have a Vanderbilt size mansion, the 6 sounds heavy. Choose your contractor and new boiler carefully. Right Mike?

    Happy Steaming.
  • Boilerpro_2
    Boilerpro_2 Member Posts: 89
    Alittle more about sizing

    Had that exact same boiler, except in water, at my former church. It heated 15,000 sq. ft. of 1850 and 1950 buildings, and was way oversized. Please get it sized right if replacing.

    Boilerpro