insufficent heat in zones

New Install:Quietside combo oil burner(120k)input(107.5k)output.5/8" nom.pextubing used.(4)zones with (1)Taco 007.f5 circulator.To heat 2k sq.ft.Hot water baseboard Suntemp-700series.Zone(1)= 21x25 w/30ft.of b/d.Zone(2)=21x25 w/30ft.of bd.Zone(3)=16x25 w/1 beacon morris kick space heater 10k btu.Zone(4)=17x15 w/18ft.of bd.Zone 3+4 being on crawl space with pex tubing not insulated.When is 20 deg.and below Zone (1,2,3)only reach 68 deg.Zone(4)only reach 66 deg. Our contractor is suggesting more baseboard.Is this the right solution ?

Comments

  • David Sutton_2
    David Sutton_2 Member Posts: 63
    Heat loss should be done

    this will let you know how much baseboard will be needed for each room, also design temp has a big play in it as well, what are the settings on the boiler? if the boiler is not running hot enuff you will not get good convection from the baseboard. insulating the pipes in crawl spaces is always a good way to go. there are a lot of factors when it comes towhy rooms dont heat up well, but all can be fixed.. good luck,i hope this helps ..David S
  • Jack Smith
    Jack Smith Member Posts: 53
    cold homeowner

    Just curious as to where you live. Contractor may be right, depending on heat loss of structure and original design criteria used. Here in WNY, the company I work for designs to 70' indoor at 20' outdoor for the heating season. If the temperature falls below the design outdoor temp., then our equipment may struggle a little, especially during prolonged periods.
  • insufficnt heat in zones

    thank you for reply boiler temp=176
  • insufficent heat in zones

    thank you,from Maryland.
  • David Sutton_2
    David Sutton_2 Member Posts: 63
    is that the running

    temp or the hi limet ???? good setting for limets are important. if there is a coil in the boiler,and you have a mixing valve you can set them at 170 - 190 15 on the diff. . if you running temp is 176 thats not that bad, if there is no coil go up to 200 on the hi limet.still get a heat loss ....David
  • Ray M_2
    Ray M_2 Member Posts: 64
    cold zones

    Dave is right,a heat loss is the first step.It's possible the pump is not moving enough water through the system when all the zones call at the same time.Did you try running one zone at a time?
    LOL
    Ray m

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • steve_6
    steve_6 Member Posts: 243
    is the boiler limiting out?

    Does your boiler shut down before the thermostats are satisfied. What are your supply and return temps?
  • insufficent heat in zones

    yes,I switched zone 4 to priority for 1hr. with no help in temp.
  • boiler limit

    yes,boiler max temp=176 it shuts down at that temp.then comes on at 155. with stats still calling. about 20" difference between supply and return. ps. circalator is on return side.
  • Ray M_2
    Ray M_2 Member Posts: 64
    cold zones

    Like i said before A HEAT LOSS HAS TO BE DONE FIRST!!!!.

    LOL Ray M

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • steve_6
    steve_6 Member Posts: 243
    heat loss

    just like has been said in other threads get a heat loss done on the house first. you may be able to solve the problem by running the system at a higher tempas D. ave said. keep us posted
  • Mark A. Custis
    Mark A. Custis Member Posts: 247
    Just a thought

    What if the heats not going any place fast due to an air blockage. New system, new water, new air.

    Mark

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Donny
    Donny Member Posts: 37
    caution

    most pex mfg'rs don't warrenty their proudct for temps over 180*