insufficent heat in zones
cold homeowner
Member Posts: 2
New Install:Quietside combo oil burner(120k)input(107.5k)output.5/8" nom.pextubing used.(4)zones with (1)Taco 007.f5 circulator.To heat 2k sq.ft.Hot water baseboard Suntemp-700series.Zone(1)= 21x25 w/30ft.of b/d.Zone(2)=21x25 w/30ft.of bd.Zone(3)=16x25 w/1 beacon morris kick space heater 10k btu.Zone(4)=17x15 w/18ft.of bd.Zone 3+4 being on crawl space with pex tubing not insulated.When is 20 deg.and below Zone (1,2,3)only reach 68 deg.Zone(4)only reach 66 deg. Our contractor is suggesting more baseboard.Is this the right solution ?
0
Comments
-
Heat loss should be done
this will let you know how much baseboard will be needed for each room, also design temp has a big play in it as well, what are the settings on the boiler? if the boiler is not running hot enuff you will not get good convection from the baseboard. insulating the pipes in crawl spaces is always a good way to go. there are a lot of factors when it comes towhy rooms dont heat up well, but all can be fixed.. good luck,i hope this helps ..David S0 -
cold homeowner
Just curious as to where you live. Contractor may be right, depending on heat loss of structure and original design criteria used. Here in WNY, the company I work for designs to 70' indoor at 20' outdoor for the heating season. If the temperature falls below the design outdoor temp., then our equipment may struggle a little, especially during prolonged periods.0 -
insufficnt heat in zones
thank you for reply boiler temp=1760 -
insufficent heat in zones
thank you,from Maryland.0 -
is that the running
temp or the hi limet ???? good setting for limets are important. if there is a coil in the boiler,and you have a mixing valve you can set them at 170 - 190 15 on the diff. . if you running temp is 176 thats not that bad, if there is no coil go up to 200 on the hi limet.still get a heat loss ....David0 -
cold zones
Dave is right,a heat loss is the first step.It's possible the pump is not moving enough water through the system when all the zones call at the same time.Did you try running one zone at a time?
LOL
Ray m
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
is the boiler limiting out?
Does your boiler shut down before the thermostats are satisfied. What are your supply and return temps?0 -
insufficent heat in zones
yes,I switched zone 4 to priority for 1hr. with no help in temp.0 -
boiler limit
yes,boiler max temp=176 it shuts down at that temp.then comes on at 155. with stats still calling. about 20" difference between supply and return. ps. circalator is on return side.0 -
cold zones
Like i said before A HEAT LOSS HAS TO BE DONE FIRST!!!!.
LOL Ray M
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
heat loss
just like has been said in other threads get a heat loss done on the house first. you may be able to solve the problem by running the system at a higher tempas D. ave said. keep us posted0 -
Just a thought
What if the heats not going any place fast due to an air blockage. New system, new water, new air.
Mark
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
caution
most pex mfg'rs don't warrenty their proudct for temps over 180*0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements