pads
Servicewiz_2
Member Posts: 28
What is the reason for pouring a pad for a boiler?
0
Comments
-
boiler pad
You don't need one,but they are nice. If the basement floods and the boiler is on a dry base out of the water,that's a good thing. The oil gun will suck dirt off the floor. I've seen the inside of an oil gun with saw dust in it already. The boiler was sitting on the floor. If you sweep dirt under a natural gas boiler,the dirt ignites and burns. Also if the boiler is elevated, it makes servicing eazy. Just some thoughts to ponder. Hope this helps.Good luck.0 -
With heavy boilers..
it may be needed to spread out the weight over a larger area (like the footings of a house). Many boilers put most of the weight of the boiler on a very small area under the legs so the pressure probably can get into the hundreds of pounds per square inch. However, as previously stated, it also just makes for a better installation.
Boilerpro
0 -
boiler pads
I like to raise oil fired boilers up on 8 inch solid blocks, makes servicing easier. Gets oil line and filter out of the way of the swing door.0 -
pads
Here in White Plains it is code to place the boiler on a pad or blocks.In fact any equipment in the room has to be raised at least 2 inches re: water heater,fan in a can ect.
lol
Ray m
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Try this:
I use two inch precast a/c slabes when possible. Most retrofits, see photo, are in unlevel conditions. I shim to level the pad pick it up and skim coat the floor with a mortor mix reinforced with an extra tad of portland cement. I can not find the fastset stuff in a form I can use. Reset the slab on the shimms to maintain level while the cement product drys and plumb away.
Mark
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
AC pads
I set a LP heater on one of those once and it melted the styrofoam out of it! Some of those are cast with white beadboard foam as a filler. For weight reduction, I suppose. It may not take the heat, if your brand is the foam filled type
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Here here...
There, there. If the boiler is not approved for installation on a combustible floor, I would not suggest using a foam filled AC pad.
The pads are referred to around these parts as "house keeping pads". Hence, their need is for house keeping. Makes it easier to clean around the boilers.
As for putting boilers not rated for use with combustible floors on a cement or gypcrete pad, I've now seen three seperate cases where the boilers combustion radiation downward caused the wood framing members on the other side of 1-1/2" of concrete to "bridge and flash" causing a fire.
There's a reason the manufacturers show the use of celluar block bases below the boiler. It's to disipate the heat so it can't do this. Follow the manufacturers instructions, or bear the brunt if something goes wrong.
JMHO
ME0 -
The ones I use are
2" solid precast concrete. No foam filled will not do at all, sorry for the miscomunication. Just a quick easy way to do the job.
Mark
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Blocking up a boiler ...
Also keeps the typical boiler drains off the floor a bit , so we can save our knuckles ! I like to use a 4X8X16 solid block under each leg . Leaves lots of room to dissapate downward radiation and a handy place for the water to go . I have also used the space for running oil feed lines . Kind of an inexpensive and handy pre-heater. Chris0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements