A bigger steam vent?
dan b
dan b Member Posts: 4
My vents at the end of the line are hissing pretty loud, and pressure is low, so my guess is that I need more of them. (I have Hoffman #75's now.) Question: is there a bigger vent out there? Given the cost of the #75, I'd like to add a bigger one rather than two or three #75s. Is there such an animal? Thanks, Dan
  • ken_6
    ken_6 Member Posts: 33
    steam vent
    check out heat timers vari vent straight or angle
    no float to get damaged from water hammer(wont stop a runaway fill)
    1/5 the cost of #75 and vents much faster(try blowing through them with your mouth)also look at heatimers lit on them
  • dan b
    question for ken
    Ken, thanks for the reply! I've got a couple of ignorant questions: (1) The heat timer website says that the vents you mentioned are for single pipe systems, and mine is two-pipe. Does that affect your advice? (2) The info on the website doesn't explain the difference between the main vents and radiator vents; it just has one picture. Are they different? (3) Do you have any idea why the Hoffman is so comparitively expensive? Thanks, Dan
  • big vents
    Look at Gorton #2 vents for your 2 pipe system. These are big, fast vents that work very well.
    Noel
    Steamhead Member Posts: 17,387
    Sizing Main Vents
    is done by calculating the amount of air in the main. We then compare that amount to what the vent will handle at 2 ounces or so.
    If you measure the length and diameter of your steam mains, we can tell you if the #75 is the right size. If you have more than one main, post the information for them all.
    If a bigger one is needed, the Gorton #2 is great. It has four times the capacity of a Hoffman #75.
    www.gorton-valves.com
    Consulting