Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Mystery One pipe problem

GW
GW Member Posts: 4,817
We took out and reinstalled a piece of BB in a commercial building to make way for a new door installed to an addition. Amazingly, the BB get's air bound every week or so, any ideas? The boiler has pressure, and no other BBs have this problem

Gary

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=171&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com

Comments

  • It depends...

    Does the system have a captive air expansion tank (bladder or diaphragm)? If it does, throw an automatic air vent at it and the problem should go away. If it doesn't, look at the possibility of supplying the baseboard off the bottoms of the horizontal mains, where air doesn't like to reside.

    Alterntaively, if the system doesn't have a captive air expansion tank, put one in anyway and install an auto vent at the troublesome BBR and at the outlet of the boiler. Get rid of the air. All of it.

    If the system doesn't have a captive air expansion tank, and you install an AAV, you're setting up a problem with the existing expansion tank and system as a whole.

    ME
This discussion has been closed.