Weil-Mclain tankless coil confusion
Paul E.
Member Posts: 7
I have a Weil-Mclain EG50 boiler running one-pipe steam in the house. I would like to add a single radiant zone, 6,000BTU heat loss, 250 ft of PEX. I thought the tankless loop option for the Weil-Mclain looked attractive - I think I could eliminate a heat exchanger and a circulator on the boiler side and simplify things.
However - I was looking thru the Weil-Mclain installation manual and on the pages where they explain installation of the tankless coil, at the top of the page they say something to the effect of "tankless coil option is only available as a factory installed item". Huh? So is it field-installable or not?
Thanks.
-- Paul
However - I was looking thru the Weil-Mclain installation manual and on the pages where they explain installation of the tankless coil, at the top of the page they say something to the effect of "tankless coil option is only available as a factory installed item". Huh? So is it field-installable or not?
Thanks.
-- Paul
0
Comments
-
I believe you have to order this boiler with a suffix T to get a section in the block with a tankless opening. If there is no tankless plate then without ordering the section and installing it in the field, you can't.0 -
But you could do the tankless
as an add-on external.
Check out www.tfi-everhot.com
0 -
Re: Weil-Mclain tankless coil confusion
I do indeed have the tankless opening w/the blank plate.
Another question - re the 3/4" center opening on the tankless coil - they say it's for a control/sensor of some sort - can anybody shed some light on this?
Thanks,
Paul0 -
If your using the tankless to make domestic hot water, which is what its intended for, then you need a control to keep the boiler at a minimum temperature during non heating season. That tapping is for that control. In your case you would mount an aquastat there and wire the relay for the heat zone through this aquastat on its way to the burner. On a call for heat the relay closes, starting the pump and the burner circuit through the aquastat.0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements