Another main vent question

jim_14
jim_14 Member Posts: 271
In that hour its heating up the water I suppose. I guess it runs until the pressure builds and turns off then turns on back again. My bills in the winter are 250-300 range (Gas&electric) same as my neighbors..

Comments

  • jim_14
    jim_14 Member Posts: 271


    My system doesnt have a main vent (long story) its 1 pipe gas fired. Its the original boiler.

    I understand the new boilers today are more efficient, smaller and generate steam much quicker than their older bretheren. If & when I upgrade to one of those new bad boys would it matter much that there is no main?

    Reason Im asking is that my neighbor (same house, year built, same builder) has a newer boiler ,maybe 10 to 15 years old compared to my 60 year old and she tells me it doesnt take long for her heat to come up in the morning. I know for a fact she doesnt have a main vent. My heat takes at least an hour of boiler running time before my rads heat up.
  • Bob W._2
    Bob W._2 Member Posts: 79
    Wow!!

    What exactly is your boiler doing during that hour it takes to heat up the rads? Where is the steam going? Assuming that the boiler is correctly fired shouldn't the steam get to the rads within minutes? It does in my system, which has large main vents and large rad vents. I keep complaining about the gas bills...if my boiler had to fire for an hour just to heat up the rads my kids would have to quit grade school and go to work in the mines:) Consider venting that sucker as an experiment. Can't hurt.
  • youv'e probably already paid to install a main vent

    many, many, times over already, except you still dont have one and the gas company has a new truck.
  • Boilerpro_2
    Boilerpro_2 Member Posts: 89
    What it is doing for an hour

    If you have one of the great big old boilers, they hold LOTS AND LOTS of water. If you turn down the heat at night, the boiler goes cold and then all that water needs to be heated up in the morning before it will start to steam. Then, if you have no main vent, it takes longer to get to the radiators. An hour from a cold start up to steam in the rads won't surprise me. Its alot faster to heat 10 gallons of water from 60F to 212F and then steam in a compact new boiler than to heat 100 gallons of water in a big old boiler when both have the same size flame. This i9s one of the ways a new boiler is more efficient.


    Boilerpro
  • Bob W._2
    Bob W._2 Member Posts: 79
    A good reason not to set the T-stat back...

    or have it come on an hour early.
  • Steamhead
    Steamhead Member Posts: 17,344
    Is that an old round \"snowman\" boiler

    like the one in the picture?

    If so, it's horribly inefficient when used with oil or gas. This type of boiler did not have much heat-transfer surface in it, and what it did have was hampered by the extremely large flue passages needed for coal firing.

    This isn't new news- one of my Dead Men's Books from the 1940s says these round boilers will probably not show an efficiency better than 40% when used with oil. And that's just while the boiler is actually running- not its AFUE.

    Venting the mains will definitely help. But you will see a big improvement when that old boiler is replaced by a new one. If you can't afford to replace the boiler now, have a good gas-conversion man look it over and install suitable bricks and baffles to slow down the escaping flue gases. This, however, is a stopgap measure at best.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • jim_14
    jim_14 Member Posts: 271
    heres a pic of the boiler in question I dont know how much

    water it holds but the service tag says steam 320 sq ft and hot water 510 sq ft
  • Joe_8
    Joe_8 Member Posts: 32
    It's alive!!!

    The old snowman lives.
  • Steamhead
    Steamhead Member Posts: 17,344
    Doesn't look that old

    unless someone repainted the jacket. And it looks like a steel tubular boiler rather than a "snowman". It shouldn't take an hour to make steam.