I'd like to know how much do these systems usually cost and how do people or companys charge(by square foot maybe? Also can these be used outside? To be more specific can they be installed into concrete bridges? How long do these systems last? What are the maintanence requirements? Well they be damaged by rain or freezing if their outside?
0
Comments
-
radiant heat
Ive heard that they have used snow melt systems in bridges in some european countries but have not found any info to support these claims.0 -
DWH for radiant heat
Can I use a domestic 40gal. gas water heater for radiant
heat in concrete that has a BTU loss of 8,699.The water heater will be used only for heat-no potable water. I need to use antifreeze in the system because it is an outside building that is approx. 12x16. Any suggestions on piping it up or any controls I should use would be much appreciated. It will be one loop about 200' 1/2"pex. How much antifreeze is needed? Also the water heater will be installed approx. 6' above the floor.0 -
I've heard
that some overpasses in Texas, maybe Oklahoma (oil country:)have melt systems installed. Maybe Watts Radiant was involved somehow. Check with them.
Maybe it was an Enron deal, and got shreaded!
When I visited the Buderus factory, in Germany, the bus driver claimed the highway we traveled on had snow melt in certain areas?? Although, when questioned, he didn't know where the boilers were located?
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
if in Canada
Not sure of USA law. But here in Canada it is now (finally) ILLEGAL to use a potable heater for dedicated heating.
So this install would not pass here..
Regards,
Terry
0 -
well it's most certainly not illegal down here, and not sure why it's illegal in canada, since there are thousands of systems working just fine with a potable water heater as their heat source....0 -
bridge snowmelt
We did a bridge snowmelt a few years ago - I believe it was in Oklahoma with a ground source heat pump as the hot water source. It was on the cover of ASHRAE Journal as I recall.
If you'll email me I can track down more information.
John0 -
Done it several times
Done it several times. I use a 30 gallon water heater, with the highest btu output I can get. You don't need the extra water, just the btus. Dial the thermostat down to the temp you want, set the circ pump up on a line voltage thermostat. You will need to oversize the expansion tank to handle the extra volume of the water heater. I have added an hour meter, just so customer knows how long it has been running. They are usually surprised that it doesn't run that much.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements