I visited a 200 room Howard Johnson's hotel yesterday at the request of the general manager; said he was running out of hot water. His boiler room is set up with an A.O. Smith BC 650 boiler with what looks like a 1,000 gal. storage tanks. The boiler runs non-stop. He's asking me for suggestions.

My first take is that boiler is too small and there's not enough storage. I've heard good things said about Aerco hot water systems from Ken Secor, Jeff Perry, Brad White, et. al., but that was quite a while ago. Are they still considered quality?

Best wishes,

Alan Forbes

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • Joannie
    Joannie Member Posts: 96
    Water Heater Sizing

    Hi, Alan.

    I plopped 200 single bedroom hotel rooms into a couple sizing guides, and they are indicating that the job is undersized. Can't be sure without more detail, but that would be the direction I'd go if I were you.

    Also, look at the piping, to deterimine if you are getting the most out of the 1000 gallon tank.

    Joannie
  • Joe Lambert
    Joe Lambert Member Posts: 18
    Aerco

    We use Aerco here in NYC, although they are usually the steam driven variety. We are impressed with the quality and have had no major problems.
  • Dana
    Dana Member Posts: 126


    I had a similar problem with this boiler. Once I determined that all the piping was ok, circ. was sized propoerly and working, I pulled the boiler apart. It was pretty well plugged up, even though it wasn't spilling co. I cleaned it and everything has been fine since. I also had a slight gas pressure problem at the manifold on one of these once. It was the meter. Gas Co. replaced the meter and it's been fine ever since. Did this system work ok at one time.
  • The owners

    just bought the place and there's no history on the mechanical equipment.

    Joan: thanks for running it through your sizing program. The piping is 2" supply and return between the boiler and storage tank; any larger sizing probably wouldn't be of much benefit since the boiler is always running.

    This is a terrible picture, but you can see two storage tanks. They used to operate off a steam boiler and have heat exchangers that have now been capped off. The top tank is valved off and they are only using the lower tank; each one seems to be about 1,000 gal. (a wild guess based on what a 500 gal. tank looks like).

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • hot_rod
    hot_rod Member Posts: 23,419
    Sizing Water Heaters for Hotels/ Motels

    Is the cover story on this months PM Engineer mag. Well written by Ron George CIPE, CPD. Check it out. Good questioneer and drawings.

    http://www.pmengineer.com/

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Thanks, hr

    I just got my copy too. Funny how these things pop up just when you need them.