snowmelt
Troy_3
Member Posts: 479
Go figure. Unhappy customer. We installed a 1400 square foot snowmelt job under uniloc pavers using a Munchkin M199 boiler. It also heats a 1000sq. ft. garage and pool in the summer. Boiler is installed mechanical is finished. Driveway goes in and we now have 3000 sq. ft. Typical! I inform owner we need at least one more boiler. We trunch the back yard to install more gas. Owner pays the gas company $1700 for a 2million btu meter. Then he tells me not to install the additional boiler till next year. Problem---He can't believe how wonderful the snow melts. It has run all winter and has never fallen behind. Question-Don't you know how to design? Why did I spend all this money to upgrade when it is not needed. I am amazed. I usually design to 150btu/sq.ft. Am I way overboard?
0
Comments
-
Tough to predict
the weather, or in your case snowfall. Generally 150 is the at the low end of snowmelt design. I have done some 125 and a couple 100 BTU/sq. ft.
Just depends on the application and exceptations. In my light snowfall area 100 is usually adequate. However a few heavy snowfalls this year strained the 100 systems. Definitely not acceptable for public walks or stairs. It may be fine for a private driveway however, if a little slush or striping doesn't impede passage.
Tough to get an accurate heatloss for the "great outdoors" I suspect if the job had fallen short and the drive or walkways slushed of fallen behind, with snow accumulation you would have heard about it also.
What type of control? Do you idle the slab or use a snow sensor for instant on?
Here is a good article describing the new ASHRAE design criteria.
http://www.pmengineer.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2732,74679,00.html
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements