Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

question foor timmie

jay_3
jay_3 Member Posts: 22

Comments

  • jay_3
    jay_3 Member Posts: 22


    is it possible to measure flame signal on spark ignition
    systems thru the ignition cable on a single probe system.
    i have a customer who is doing it this way. i did explain the proper way. reading off of the burner ground terminal but he still wants to know if it's possible the other way?!
    thanks, jay k.
  • It is possible

    but not recommended as the high voltage spark may damage the meter. The reading on some system may also not be accurate.

    Single rod systems are proprietary to Honeywell and because of the way the sense signal and the spark are out of phase it can be done.
This discussion has been closed.