Broken Union Test

Bill_3
Bill_3 Member Posts: 34
Hey Dan, In Al Levi book operating power, one page 9-7 For Automatic Feed Boilers, what is the Broken Union Test.

Comments

  • tombig
    tombig Member Posts: 291
    Broken Union Test

    Unpipe the union downstream of the water feeder to if its dribbling water into the boiler causing it to overfill over time. If theres no union, there should be.