Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Broken Union Test

Options
Bill_3
Bill_3 Member Posts: 34
Hey Dan, In Al Levi book operating power, one page 9-7 For Automatic Feed Boilers, what is the Broken Union Test.

Comments

  • tombig
    tombig Member Posts: 291
    Options
    Broken Union Test

    Unpipe the union downstream of the water feeder to if its dribbling water into the boiler causing it to overfill over time. If theres no union, there should be.
This discussion has been closed.