new system injection problem

pat_3
pat_3 Member Posts: 89
after changing injection pump ,everthing works fine ,injection pump no longer running at full output.thanks

There was an error rendering this rich post.

Comments

  • pat_3
    pat_3 Member Posts: 89
    new system injection problem

    system is less than a year old.entire home is radiant heat,suspended floors,tube is embedded in mudd job throughout.btu load of about 75,000.piped primary/secondary,1 inch primary,3/4 injection lines,1 inch beyond injection lines with 3/4 secondary loops to various manifold locations.injection controlled with a tekmar 356.tekmar 356 indicates 90% output from variable speed pump continuously and doesnt seem to be able to reach current desired mix temp.boiler does not seem to have problem reaching aquastat setting.rooms not satisfying since temp went below 20 3 days ago.

    There was an error rendering this rich post.

  • marc
    marc Member Posts: 203
    injection piping

    sounds like there are a few things wrong.tekmar essays say injection piping to be at least 1 pipe size smaller than both boiler and low temp loop. 3/4 in. inj. piping is huge. also tee spacing on primary secondary piping and on low temp loop. what size pump on inj. we use the 356 all the time. if piped correctly they will perform perfectly.
  • kevin
    kevin Member Posts: 420
    what is..

    the boiler temp? what is the primary suppy temp and return temp? Any baseboard loops? I had a problem like this just the other day.The boiler was not putting out 180/185...even though the boiler gauge said it was 180 it was in reality 165...kpc
  • pat_3
    pat_3 Member Posts: 89
    new system injection problem

    injection piping is 1 pipe size smaller than boiler piping as well as low temp secondary header.pump is b&g nrf22,was throttled back on inj line until today.

    There was an error rendering this rich post.

  • pat_3
    pat_3 Member Posts: 89


    boiler temp aswell as primary supply temp 180,seems to cycle fine,just cant reach mix target temp

    There was an error rendering this rich post.

  • kevin
    kevin Member Posts: 420
    is there...

    a boiler minimum temp. If so what is it set to.
    Try boosting your boiler temp. to 190* kpc
  • pat_3
    pat_3 Member Posts: 89


    i dont think boiler temp is going to make that much of a difference.i didnt design or install the system,homeowner cant contact plumber that did.i dont know for sure what was done with the tubing layout but everthing i can see in the boiler room seems ok except mix temp seems to be about 20degrees off target.

    There was an error rendering this rich post.

  • eleft(retired)
    eleft(retired) Member Posts: 98
    new system

    If you have a throttle valve in the variable speed injection return open it so the pump reaches 100% then reset after it reaches desired mix temp.

    al
  • pat_3
    pat_3 Member Posts: 89


    opened throttle valve all the way,mix temp still didnt reach target temp

    There was an error rendering this rich post.

  • eleft(retired)
    eleft(retired) Member Posts: 98
    target temp

    It takes a while

    al
  • pat_3
    pat_3 Member Posts: 89


    thanks for your input al ,i'm thinking that maybe the flow rate on the secondary side might be too great for injection lines and pump to keep up with,if mix temp isn't achieved with throttle valve full open over night,i'll check delta t's on secondary loops and maybe throttle them back if possible.what do you think?can it be possible the water is moving so fast on the secondary side that its not picking up enough heat off the injection line.i've never seen this happen before.can't be the boiler right?if the boiler was under sized it wouldn't reach high limit?

    There was an error rendering this rich post.

  • Patrick_3
    Patrick_3 Member Posts: 20
    Had the same

    problem this week on a new installation. It has been running fine up until a few wks ago. What I thought could not be happing, was. My injection loop was back flowing and just recirculating within itself and not drawing 180* water from boiler. All due to the screen of my y-strainer being plugged with flux and debris. I removed the screen and system is working great. Good luck, Patrick
  • eleft(retired)
    eleft(retired) Member Posts: 98
    Boiler not a problem

    Pat,

    Are you getting 100% V/S pump speed?

    Are you on out door reset mode?

    If so what temp? (you might need to raise it to start the heat curve higher ending up with a higher supply temp)

    Is your ratio set correctly to achieve the temp you want at the colder than expected out door temp? (if on out door reset)

    Is your supply temp set higher than the temp you want?

    al
  • kevin
    kevin Member Posts: 420
    i didn't..

    ask if the boiler size was too small. Iwas asking if the boiler temp was high enough. This just happened to me the other day boiler temp was too low. (8148 was wrong) as soon as I turned up the temp the injection loop zone came up to temp.kpc
  • pat_3
    pat_3 Member Posts: 89


    tekmar 356 says 90% output which i believe is the highest indicator.i am on outdoor reset,outdoor design temp was set at zero ,i bumped it up yesterday to twenty and it didnt make a difference,thats when i realized i wasnt maintaining desired mix temp regardless of outdoor design temp setting,mix temp only seems to be getting to about 86degrees...should be around 105,125 with bumped up outdoor design temp.if it was an older system i would think the injection pump was bad.

    There was an error rendering this rich post.

  • pat_3
    pat_3 Member Posts: 89


    kevin,boiler temp is set at 180 and actually is 180

    There was an error rendering this rich post.

  • hot_rod
    hot_rod Member Posts: 23,185
    Are you sure

    the injection pump is spinning? May be time to pull it out and check. Could have a broken shaft, plugged impeller?

    Is there a throttle valve on the injection riser? You may switch the tekmar control to setpoint mode and see if it reaches target.

    In cold start up , it takes time to ramp around.

    Doubtful the secondary pump is moving thre water too fast!

    hot rod

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • eleft(retired)
    eleft(retired) Member Posts: 98


    Pat,

    Do you have this?
  • pat_3
    pat_3 Member Posts: 89


    pulled the pump ,looked fine ,replaced it just to make sure.system now runs the way it should.thanks to everone

    There was an error rendering this rich post.

  • pat_3
    pat_3 Member Posts: 89


    pulled pump,looked fine,replaced it just to make sure.system now running the way it should.thanks to everyone

    There was an error rendering this rich post.

  • Steve Eayrs
    Steve Eayrs Member Posts: 424
    check the sensors.

    I have run into a few sensors going bad. You can ohm them and test according to the spec sheets. I know you checked the injection pump, but what about the system pump? This would explain the injection running full bore, if you don't have circulation on the slab pump. Whats actual temp. at slab sensor?

    good luck, Steve