hot water heater/boiler
hot_rod
Member Posts: 23,184
Most anode rods are aluminum or magnisum. Hydronic system antifreezes don't get along well with these metals. With a sealed system and a good inhibitor package in the antifreeze, really there is no need for the anode.
Also 25% is the very minimun you should blend hydronic antifreezes. Below that your inhibitor package is getting too weak. You may consider boosting the inhibitor package. Boost kits are available fromthe manufacture of the antifreeze.
Remember the inhibitors are in there to "handle" the blend water, not the glycol.
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
Also 25% is the very minimun you should blend hydronic antifreezes. Below that your inhibitor package is getting too weak. You may consider boosting the inhibitor package. Boost kits are available fromthe manufacture of the antifreeze.
Remember the inhibitors are in there to "handle" the blend water, not the glycol.
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
0
Comments
-
antifreeze
What will happen to the anode in a water heater being used as a boiler with 25% antifreeze? Should it be taken out?It is only 6 gal. Bruce0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements