Cool Tool (Steamhead)

Options
Steamhead
Steamhead Member Posts: 16,866
at NAPA auto parts stores for less than $100. Or order online at www.raytek-northamerica.com .

Here I'm measuring the return, again with the boiler off- 83 degrees. Delta-T tends to equalize when the boiler is off- it's 10 degrees when the boiler is running. This with the slower circulation achieved by changing the B&G 100 to a Taco 005. It will be interesting to see what happens after I install the B&G NRF-9.

Outside temperature was 24 degrees when I took these readings. Indoors was 62- I don't need it to be higher. Radiators measured 89 degrees.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting

Comments

  • Steamhead
    Steamhead Member Posts: 16,866
    Options
    Raytek MiniTemp

    is a point-and-shoot infrared thermometer. The MT4, shown, has a built-in laser aiming device- the MT2 does not. Here, I'm measuring the temperature of the flow pipe on my gravity-converted hot water system- 89 degrees. The boiler was off at the time.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Don_2
    Don_2 Member Posts: 47
    Options
    What!!

    How can you afford that thing? I thought you already spent
    all your money on those antique phone....hehehe
  • Steamhead
    Steamhead Member Posts: 16,866
    Options
    Nope

    that's why I negotiated with that guy! Have to have something left over for cool tools ;-)

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Boilerpro
    Boilerpro Member Posts: 410
    Options
    Hey Steamhead

    Twas wondering at what load does your system run that 10F delta tee. The delta tee changes with the heating load on thesystem. In cold weather you will see a higher delta tee and in warmer weather a lower delta tee.

    Boilerpro
  • jim f
    jim f Member Posts: 182
    Options
    accuracy

    i purchased one of those in the summer to check suction line temps on ac systems to calculate superheat....found it very inaccurate compared to my strap on temp sensor...wondering if this was due to outside temps or copper??? but i have used it to check delta t's across supply and return temps in hydro-air systems with good luck
    jim f.
    milford, ct.
  • Chris_4
    Chris_4 Member Posts: 75
    Options
    Jim

    If you are using it to check copper, you should put a piece of black electrical tape on the copper before reading the temp, otherwise you will get inaccurate readings from the copper.

    Chris

  • John@Reliable
    John@Reliable Member Posts: 379
    Options
    Jim, I find that you must

    only use on painted pipe or fittings if copper. I spray what I want to check w/a quick shoot of flat black paint. John@Reliable
  • Steamhead
    Steamhead Member Posts: 16,866
    Options
    Good question!

    I've never done a full heat-loss on this house- kind of like the shoemaker's kids having the worst shoes in town, eh? All in good time. I did reduce the firing rate from .85 to .75 GPH this past fall, since the burner was really short-cycling with the increased heat-transfer efficiency brought on by the smaller circ.

    The delta-t can be measured across a radiator too, not just on the mains. This can give you an idea of just what's going on inside the rad, and how much heat is going into the room. As I write this, it's 27 degrees outside and 62 inside, and the last rad on the long loop is 91 degrees at the inlet and 81 at the outlet. This averages out to 86 degrees, which would put out about 75 BTU per square foot EDR. The rad is 52.5 square feet, so the room is getting 3937.5 BTU per hour.