handle the air with a good main vent/keep rad valves open and level rad to pitch back to pipe/ keep steam pressure as low as possible 1main 1/2differential use adjustable steam vents/ handle the air/stay warm and quiet
0
Comments
-
I have a 100 year old house with a single pipe steam radiator system on a 2 1/2 year old oil fueled furnace.
I have four radiators that did not always heat when the system fires up. Sometimes they would, sometimes they wouldn't. I have replaced the vents on all 4, but the problem remains on three of the four.
Any suggestions?0 -
Is there a
main vent on that steam main somewhere ? If there is , has it been changed recently ? We see quite a few houses without em , and the ones that do have em are piped usually in the wrong spot - which makes replacing them a yearly service .0 -
You may have re[placed vents...but
that doesn't mean that they are good ones or the right size..and yes main vent a must Mad Dog
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Has
the insulation on the steam supply lines been removed or falling off? this adds extra load to the boiler and sometines the steam just cant make it all the way out.
p.0 -
I agree.
What Joe said.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements