Once Gravity, Always Gravity?
Tom Minzenberger
Member Posts: 6
Thanks for your comments Steamhead! That sounds like good advice. I'll pitch them to the customer and post the rusults. Thanks again!
tminz
tminz
0
Comments
-
I' ran across an interesting gravity hot water system the other day. The piping system has a 3" main traveling around the basement with all the radiators being supplied with warmer water coming directly off the top of the main and the cooler return water sliding directly into the side of the main.
I have seen this type of gravity system once before with the original boiler still in place and still doing a wonderful job keeping the home comfortable. This latest system, however, some years back had its boiler replaced, and the mechanic who did the job installed a circulator at the new boiler. I'm not quite sure, but I can't see how this can heat the home as well, from a comfort stand point, as if there was no circulator, and the boiler piped in to allow gravity flow. The customer is complaining of some areas of the house not heating as well as other areas.
Any thoughts on this matter would be greatly appreciated.
tminz0 -
That's a One-Pipe Gravity System
which wasn't too common except in small buildings.
My guess is the water is moving too fast thru that main, so the hot water doesn't rise to the radiators as it should.
Try using a smaller circulator. If you have a Taco 007, try a 005 or B&G NRF-9. Slow down the flow and I'll bet it works better.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
> which wasn't too common except in small
> buildings.
>
> My guess is the water is moving
> too fast thru that main, so the hot water doesn't
> rise to the radiators as it should.
>
> Try using
> a smaller circulator. If you have a Taco 007, try
> a 005 or B&G NRF-9. Slow down the flow and I'll
> bet it works better.
>
>
>
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 157&Step=30"_To Learn More About This Contractor,
> Click Here to Visit Their Ad in "Find A
> Contractor"_/A_
> which wasn't too common except in small
> buildings.
>
> My guess is the water is moving
> too fast thru that main, so the hot water doesn't
> rise to the radiators as it should.
>
> Try using
> a smaller circulator. If you have a Taco 007, try
> a 005 or B&G NRF-9. Slow down the flow and I'll
> bet it works better.
>
>
>
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 157&Step=30"_To Learn More About This Contractor,
> Click Here to Visit Their Ad in "Find A
> Contractor"_/A_
0 -
> which wasn't too common except in small
> buildings.
>
> My guess is the water is moving
> too fast thru that main, so the hot water doesn't
> rise to the radiators as it should.
>
> Try using
> a smaller circulator. If you have a Taco 007, try
> a 005 or B&G NRF-9. Slow down the flow and I'll
> bet it works better.
>
>
>
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 157&Step=30"_To Learn More About This Contractor,
> Click Here to Visit Their Ad in "Find A
> Contractor"_/A_
0 -
That's what I was thinking. Any chance that the Bell&Gosset 2" Flo-Control may have some trouble opening if I used either of those circulators mentioned? I might add that there have been additional zones added to the system so removing the Flo-Control is not an option.0 -
If you have trouble with that flow-check opening
try installing a smaller one, which wouldn't take as much effort to open. But I doubt it will be a problem.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
One Pipe Gravity
I reworked one of those guys a few years back. The return tees on the 3" main teed horizontally at the bottom of the fitting. First and only time I've seen an ECCENTRIC tee. Had to be cast specifically for this application. I zoned the house so I kept the 3" as a return loop and piped new supplies for 1st and 2nd zones. Tombig0 -
One Pipe Gravity
I reworked one of those guys a few years back. The return tees on the 3" main teed horizontally at the bottom of the fitting. First and only time I've seen an ECCENTRIC tee. Had to be cast specifically for this application. I zoned the house so I kept the 3" as a return loop and piped new supplies for 1st and 2nd zones. Tombig0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements