expansion tanks

Options
steel exp tanks should be drained every year sorry only thing that seems to work and not cause air to move out into the system has to do with heat rising and cold falling in the line hooked to the tank causing waterlogged condition you cant tell by tapping we drain every year needed or not drop pressure to 0 on system to ck bladder tanks as far as i am concerned if it has lost air pressure you will have problems [thats why you are there right] do it now or at 3am your choice by the way...leave that feeder wide open? hope that relief reseats read the literature with a prv

Comments

  • paul_14
    paul_14 Member Posts: 16
    Options
    expansion tanks

    what indications would show if a expansion tank was bad besides tapping on it to tell if its waterlogged or not?
  • Jackchips
    Jackchips Member Posts: 344
    Options
    You will

    get periodic water from the relief valve (water on the floor) and your boiler will be running at a much higher pressure.
  • hot_rod
    hot_rod Member Posts: 22,193
    Options
    If it's a bladder type

    push in the valve stem on the bottom. Water or air??

    hot rod

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Tom_7
    Tom_7 Member Posts: 32
    Options
    Expansion Tanks

    I been told that if you drop the pressure in the boiler to zero. You can test the extrol tank with a tire air gauge if its less than 12 lbs its no good.
  • zeb_3
    zeb_3 Member Posts: 104
    Options
    E- tank

    You can test tank pressure by dropping boiler press. to zero. Diaphram tanks will lose press. through the diaphram over time. A drop in pressure does NOT necessarily mean it is no good. Simply add air to tank, if it holds your OK, if not replace it.
  • Greg Steger
    Greg Steger Member Posts: 2
    Options
    bladder tank good or bad

    I was always under the impression that if a bladder tank was bad that you would find the air side of the tank waterlogged. Is this right or wrong thinking?
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,538
    Options
    Solution to that

    is the Bell & Gossett Airtrol Tank Fitting, a amazing little device.
    Retired and loving it.
  • zeb_3
    zeb_3 Member Posts: 104
    Options
    greg

    if there is H2O on the air side it is BAD. BUT if the pressure is not there and there is NO water, you can "RECHARGE" it w/ air