Very simple question here...do the air vents have to be right-side up, or is upside-down acceptable?
After tightening this new vent, it was upside-down and I'm also not getting any steam/heat from that radiator, although it's the nearest to the boiler room?!?!
After tightening this new vent, it was upside-down and I'm also not getting any steam/heat from that radiator, although it's the nearest to the boiler room?!?!
0
Comments
-
vent
must be upside right0 -
Vent must be UP.
The vent must be up because air wants to sit at the high point. The vent down defeats the purpose.
Tom Meyer
Senior Designer/Trainer
Precision Hydronics
www.precisionhydronics.com0