A building I am working on had a 2 pipe steam radiator with no heat. When I loosened the nut on the union to the radiator steam trap, the condensate line emitted air for a long time. Then the radiator heated up. The following apply:
-The steam is supplied from the utility co. The condensate drains by gravity to a condensate tank, where it is vented and is pumped to a drain.
-Although the return lines are old, they are clean inside.
-The return line has dips and is not pitched uniform to the condensate tank, which is far away.
-Should I install an air vent on the return line? Do vents belong on 2 pipe systems?
-The steam is supplied from the utility co. The condensate drains by gravity to a condensate tank, where it is vented and is pumped to a drain.
-Although the return lines are old, they are clean inside.
-The return line has dips and is not pitched uniform to the condensate tank, which is far away.
-Should I install an air vent on the return line? Do vents belong on 2 pipe systems?
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements