cast iron baseboard
Gordo
Member Posts: 857
to be heated with circulated condensate from steam boiler in basement. Does anyone here have any experience using CIBB in this application? Any problems purging the air out? Any problems with air leaks? Customer only wants cast iron, thinks the finned stuff looks cheap and tacky. What the customer wants....Would try to heat it with steam (2 pipe), but there's 21 feet of the stuff, and only 5 feet gets hot, which, as I understand it, is the max. for steam in baseboard. Thanks for any insights.
click...
the Heating Q&A line on the pipe on the side. Checkmout the Condensate heating section. Lots of good stuff... kpc0 -
Yes, thank you, however,
I've read Dan's book "How Come". My questions are about using cast iron baseboard with this system. Has anyone used CIBB in this application successfully?All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
Only 5 feet
I have an installation with one pipe steam with upward 12 feet of CI baseboard and works fine (even though it should be banging but never does). The units I have seen only have 3/4 inch tappings and this may be your problem. Are the other radiator feeds this small. If not the 3/4 inch tapping is acting as an orifice, restricting the flow of steam to the baseboard. Throttle back on the other rads some and it should heat more completely, if this is the problem.
Boilerpro0 -
Whys it matter
If its castiron or copper baseboard.The only problem I could see is that castiron might override the tsat a bit.
I think the thing to worry about here is keeping the water below 180 degree so it wont flash to steam. Are you going with the heatexchanger or no heatexchanger?0 -
yep, only 3/4\" fittings
and leaking in several places, so it has to be replaced. Very hard to pitch, being so long, and there are carpentry issues (moldings and such) that the customer doesn't want touched. There are two other long runs of CIBB in the system and only 5 feet or so on them gets hot (3/4" fittings also). The two short runs of CIBB heat just fine. And one of the other long runs of CIBB just started leaking. Figure I can repipe to heat all the long runs with condensate.All Steamed Up, Inc.
Plan to use bypass
and thermometer to keep temp below 180*F, by the book, as they say. No heat exchanger use is being contemplated at this time.All Steamed Up, Inc.