Optimizer Schmatics

Fellas:

Anybody have any schmatics of the carrier optimizer?
Anybody have any idea how this thing works?
Sorry about the spelling.

Thanks
John

Comments

  • Dan Foley1
    Dan Foley1 Member Posts: 55
    Carrier

    Which one? Carrier made an Optimizer I, Optimizer II and the new Optimizer logic built into their electronic dual fuel tstat. I probably have schematics on all of these. Let me know which one you need. -DF
  • John G. Merritt
    John G. Merritt Member Posts: 140
    Optimizer 1 & 2

    Dan, I need 1 & 2. Not familiar with newer one.

    John
  • EDDIE GRIERSON_2
    EDDIE GRIERSON_2 Member Posts: 32
    INFO.....

    The 1 used an O.D. stat with a isolation relay on the O(reversing valve). They did not hook up W2 at tstat. They took Y from t-stat to OD stat which either went to contactor or furnace depending on setting and temp. They take O (from tstat) and common to coil side of relay. They take R and O (to heat pump) to the normally open relay contacts. This prevents backfeed. They do this to prevent furnace and H/P from running together. Make sure H/P has high pressure switch. GOOD LUCK