Tekmar 363 problem

Markus
Markus Member Posts: 9
once more I have to ask for the help of all the great people here on the wall.

My system is: Outdoor wood boiler, back up Propane, 4 Baseboard zones, 1 domestic HW zone. HX between Outdoor and Indoor system. Controled by Tekmar 363.
everything worked fine for the last few months, then yesterday the control started to get all the heat from the Propane boiler. and it wont switch back to the outdoorboiler. there is enough heat out there, and I dont understand why it wont switch back.
When i run a test on the Tekmar unit, everything works fine. no error message displayed.
can you help....??...

Comments

  • hr
    hr Member Posts: 6,106
    Check the sensors

    I have had a few bad ones lately. The installation manual gives you the resistence readings for checking them. An ohm meter will be needed.

    Also check connections, look for a broken wire at the terminal strip. Often solid thermostat wire will break, at the end, if the wire stripper cut to deeply.

    Pretty easy for a wire to come lose or slip out of that small terminal strip, check there also. Tekmar has a good tech support number also.

    hot rod

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Markus
    Markus Member Posts: 9
    cant find

    cant find any loose wires or bad sensors, i'm getting frustrated.
    Hope that Tekmar is working tommorow.
    and of course it has to happen right at christmas so it can spoil the whole good time
  • Terry
    Terry Member Posts: 186
    363

    How is the 363 wired to this system ?? I read up on 363 & see nothing pertaining to separate heat sources. Only 1 set of boiler contacts. Perhaps a diagram or description of how this unit is wired would help in determining your problem. Not a good thing @ Christmas ?!?.

    Regards,
    Terry
  • Mike Lampkin_2
    Mike Lampkin_2 Member Posts: 124
    Check for a switching relay...

    Hi Markus,
    There has to be some kind of swithing relay controlling
    which boiler should be operating. If the water temperature
    in the wood boiler drops to a certain setpoint, then the
    aquastat should signal the propane boiler to take over.
    There may be a faulty transformer or relay causing the
    problem.If everything works fine with the propane boiler, I
    would not suspect the 363. Not being able to see the wiring
    diagram, I'm just guessing.
    Merry Christmas
    Mike Lampkin
  • Markus
    Markus Member Posts: 9
    Thanks

    Thanks for all the help. Everything running ok again. Must have been a bad contact after all. And of course it healed it self as I was just going to dial the Tekmar number.
    And once more Mike from Tekmar here in BC was a big help.
    Thanks to all of you who tried to help me.
    All the best from the West, Markus