Globe or ball valve
For balancing a VSIM system, which do you prefer, a globe valve or a ball valve? And, why? Just curious.
Chuck Shaw
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Chuck
The valve of choice is a globe valve. Does a better job of throttling the flow. Less restriction at low flows than a ball.0 -
Best bet
Is to use a valve built just for that application. I have used both ball and globe. But for a few extra bucks get a valve built for throttling with a flow meter. No guessing involved. This has a nice tapered valve and seat for easy, fine adjustments.
Ball valves on VS don't seem to do much until the last little bit of handle movement. Then the tinyest movement makes a big change. Real hard to be accurate. Also the ball presents a sharp edge to the fluid flow. Not ideal! Globes are better but still not a perfect flow adjuster.
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
This one
came from Watts Radiant. They only offer one size, however in their catalog. ISTEC shows a better selection of sizes and flow ranges at www.istec-corp.com.
A bit of pressure drop through the valve, no doubt. Generally VSIM applications have pump head to spare
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Thanks, HR (nm)
0 -
Valve choices
Hi Chuck,
A globe valve or circuit setter are the best options for controling an injection loop. They have good "Valve Authority". This means that the relationship of flow to the valves position is close to equal. A ball valve on the other hand has poor authority which means that it must be closed very far to effect the flow at all and it is not in equal proportions. Hope this helps.
Tim D.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements