Does anyone have a picture
KCA_2
Member Posts: 308
Of the effects of condensate on a flue or heat exchanger?
Thanks
:-) Kca
Thanks
:-) Kca
:-) Ken
0
Comments
-
Condensation
pictures:
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Thanks!!
You da man!!
:-)
Kca:-) Ken0 -
Eating up the education
Alan, I'm just wondering and trying to learn at the same time. So I have a question. I'm sure that most of that was caused by a low stack temp and possible an inadequate vent system.
But I noticed in one of the photos (MVC-003F.JPG) There was no drip leg at the gas valve. Is it possible that this contributed to adding moister through the combustion process increasing the amount condensation? Remember what I know about gas you could fit in a thimble But I love learning! Thanks
Your friend in the industry,
Alan R. Mercurio
Oil Tech Talk0 -
no liner
0 -
no liner
Lost this job a few years ago low bid apparently didnt think a liner was needed.0 -
Pacific Gas and Electric
is our local gas supplier and they guarantee delivery of natural gas that is moisture free.
This job was really an anomaly 'cause I've never seen a boiler condense this badly.
All the best,
Alan
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Any idea...
what the culprit was on that little Lochinvar? I sure don't like the flue reducer - that's a no-no in my book.
We did a couple of jobs with oversized boilers and had real condensation problems in outside exposed chimneys. One had moisture just oozing out of the brick. On both, a flexi liner solved the problem. Getting a 6" liner down a 6 1/2 x 10 tile liner is murder though!0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements