Expansion tanks

Pete_2
Pete_2 Member Posts: 5
I have an oil fired hydronic system that keeps popping the relief vavle. I mistakenly assumed that the valve was bad and replaced it. You guesses it....it still leaks. There is an overhead expansion tank and i fear its waterlogged but i am not sure what to do with it. It is an plain old tank not the new diaphram type. I was told just isolate the tank and drain it completely than reopen the vavle to the system.

Comments

  • zeb_3
    zeb_3 Member Posts: 104
    Yup

    That will replenish your "air cushion" in the e-tank. This is something you will have to do periodically.
  • Pete_2
    Pete_2 Member Posts: 5
    haha

    Well than Im about 20 years overdue!
  • Pete_2
    Pete_2 Member Posts: 5
    hmmmm

    so thats the proper proceedure.....should I do it hot or cold or does it matter? Its actually my Moms house and Im sure its had no TLC since my Dad died. He was the expert at these things!
  • J.C.A.
    J.C.A. Member Posts: 349
    sounds like ....

    It works for your system . O.K. , fess up ....how many of us have seen a diaphram tank last 20 years ?

    I've only been at the game for 18 but still haven't seen 1 go that long .
  • Eric
    Eric Member Posts: 95
    Air management vs air removal

    Did anyone add any automatic air vents or any other changes to system?
  • Pete_2
    Pete_2 Member Posts: 5
    older than that....

    The system was put in in the late 50's! Its all original except for a new circ pump and last year I put in a new auto fill and added a backflow preventer after my brother "bled" the air not to mention almost all of the water out! 40 some odd years later it still looks like it was installed yesterday. my dad was obsessive about cleaning it inside and out and maintaining it. The oil guy even took pictures of it last year!
  • nerski
    nerski Member Posts: 6
    Eric

    Good call on the air vents. I just learned that myself.
  • zeb_3
    zeb_3 Member Posts: 104
    Hey Pete

    Did your dad ever have to tend to the e-tank?
  • Pete_2
    Pete_2 Member Posts: 5


    Im sure he did but its been a few years since he passed and he wasnt too sharp the last couple so even if he did its been a while.