Saw my first vacuum system yesterday

Options
No official age listed but room trim & rads make me believe 1920s.

Saw "strange looking devices" on the returns and return pipe was smaller than supply so presumed it was a vapor/vacuum system. No air vents on rads whatsoever. Hightailed it to the basement. Seemed to be confirmed by gauges/devices on boiler.

Saw what I believe to be a couple of large "standard" air vents hanging around near the boiler and a couple other connections nearby these vents that were plugged. Vents didn't look as old as rest of system--nor did plugs.

Should it have been under vacuum?

Am used to seeing big old boilers around here but this one was a monster--cylindrical about 4' diameter & 5' high. Looked in perfect shape save the crudy, filthy sight glass. House not too big--2 full floors--about 28'x36'.

Comments

  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Options


    Not to service but being nosey at open house in old home built around same time as mine.

    Rather warm outside so it hadn't been running (much). Vacuum gauge read 0 (atmospheric pressure).

    Cut-in set at 2#, differential at 4#.

    Aren't they supposed to hold a vacuum? Is the system working off "regular" steam?

  • Steamhead
    Steamhead Member Posts: 16,860
    Options
    It's probably Vapor

    if the original vacuum vents were replaced with standard vents, it won't dip into vacuum. Still a great system though! Do you remember who made it, such as Trane, Webster, Dunham etc?

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steamhead
    Steamhead Member Posts: 16,860
    Options
    Reuben Trane must be smiling from Heaven

    at the sheer number of old Trane Vapor systems we've found and restored.

    That "snowman" boiler was about 60% efficient on coal, worse on oil or gas. If there was no Return Trap there (looked like an old metal milk jug), the connections were probably plugged when the Return Trap was removed.

    The original Trane vents were vacuum-type. No need for vacuum on an oil- or gas-fired system so that explains the standard vents, and the system not dropping into vacuum.

    You did leave them your card, didn't you?



    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steamhead
    Steamhead Member Posts: 16,860
    Options
    Reuben Trane must be smiling from Heaven

    at the sheer number of old Trane Vapor systems we've found and restored.

    That "snowman" boiler was about 60% efficient on coal, worse on oil or gas. If there was no Return Trap there (looked like an old metal milk jug), the connections were probably plugged when the Return Trap was removed.

    The original Trane vents were vacuum-type. No need for vacuum on an oil- or gas-fired system so that explains the standard vents, and the system not dropping into vacuum.

    You did leave them your card, didn't you?



    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steamhead
    Steamhead Member Posts: 16,860
    Options
    Reuben Trane must be smiling from Heaven

    at the sheer number of old Trane Vapor systems we've found and restored.

    That "snowman" boiler was about 60% efficient on coal, worse on oil or gas. If there was no Return Trap there (looked like an old metal milk jug), the connections were probably plugged when the Return Trap was removed.

    The original Trane vents were vacuum-type. No need for vacuum on an oil- or gas-fired system so that explains the standard vents, and the system not dropping into vacuum.

    You did leave them your card, didn't you?



    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steamhead
    Steamhead Member Posts: 16,860
    Options
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Options
    Butter Churn

    What I presumed was the collection device looked sort of like a slender butter churn when connected. Air vents? nearly directly above.

    Need to bring my Starbuck green book here--believe I remember a similar system illustrated.

    Why no need for vacuum on an oil/gas system? How can it produce "vapor" without lowering the pressure?
  • Steamhead
    Steamhead Member Posts: 16,860
    Options
    \"Vapor\"

    in this case is actually steam at a few ounces above atmospheric pressure. Most of these systems were designed to max out at 8 ounces or so.

    The reason vacuum doesn't work well on oil or gas is that the system often goes into vacuum before all the air is out. When this happens, the remaining air can expand enough to block steam flow.

    If there's a vent right on top of the "butter churn" it's a float trap/air eliminator, not a return trap. See the "Here's my Trane" post for a look at one. That system also uses water seals on the rads instead of traps.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting