Boiler emergency kill switches
Bryan_2
Member Posts: 1
Controls and Saftey Devices
0
Comments
-
Standard Building Code
Is anyone familiar with a requirement to have an emergency boiler kill switch at boiler room exits? I refer to a "mushroom" type big button that will kill all boilers in the room when pressed.
Specifically down south in the Standard Building Code/Standard Mechanical Code jurisdictions.
If so, can you point me to where the requirement might be found?
Thanks.
0 -
Could it be ...
that you are refering to CSD-1?
It does require a "kill" switch (not necessarily a push button mushroom type) outside the boiler room door.
CSD-1 applies to larger boilers (>400 MBH) and has been adopted in several southern states.
Does this help?
Bill Wright
Manager, Radiant & Plumbing Systems
Weil-McLain0 -
I don't recognize that acronym - CSD. Can you help?0 -
CSD-1
ANSI/ASME -- Controls and Safety Devices for Automatically Fired Boilers. A national code, that has been adopted by many states. Applies to larger boilers >400,000 Bth (does not apply to residential).0 -
More CSD-1 info ...
Here is a website:
http://www.nationalboard.org/article3.html
& I will attempt to attach a spreadsheet that lists all the states that have adopted CSD-1.0 -
Thank you everyone!
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements