Risers

Tim_14
Tim_14 Member Posts: 23
My boiler has two 2" supply tappings.
Can I run a 2" off set riser bushed into a 3" header or does the off set riser have to be 3" also.
TK

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    You can do it

    the way you suggest. The steam will slow as it reaches the header and that will help to dry it out.
    Retired and loving it.
  • Steamhead
    Steamhead Member Posts: 17,385
    Be sure

    the top of your riser is at least 24-inches (or whatever the boiler manufacturer specifies) above the highest possible water level in the boiler. This will also help keep the steam dry since water can't usually rise that far.

    If you run out of headroom, a "drop header" is the solution. Here's one that Noel built. See how tall the risers are?