    boiler pressure and heat exchange

    Would heat transfer within a boiler be adversely affected by a boiler pressure above 12psi. Obviously pumping efficiency falls, but does the heat transfer slip as well?
  • Steamhead
    Steamhead Member Posts: 17,343
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • greg_7
    greg_7 Member Posts: 71


    Duh... I tried to make the question as simple and direct as possible. Oh well.

    Hot water.
  • Steamhead
    Steamhead Member Posts: 17,343
    Shouldn't affect it

    The only reason you need pressure at that level is to make sure the water fills the system to the top. Pressure does not affect circulator efficency- what goes up must come down, and the two balance each other out. Picture a Ferris wheel- the principle is the same.



    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • greg_7
    greg_7 Member Posts: 71


    I'm not concerned about the circulator...only about the effect of pressure on heat transfer from the boiler to the water, if sny.
  • Yes.....somewhat

    Greg,

    What does change with pressure increase is the saturation temperature of the water at the walls of the boiler sections in contact with the 1100°F flue gasses. I can't remember the exact perameters, but as I recall, that temperature would be about 250°F at 30 psi and well in excess of 300°F at 80 psi. I have a chart somewhere with the exact numbers. Hope this helps.

    Glenn Stanton

    Burnham Corp.
  • greg_7
    greg_7 Member Posts: 71


    Aha! I knew it. Would it follow that a lower pressure, such as the 12 or so for the average homeowner, have a similar drop in saturation temp?

    Do you design for an optimum or an industry standard.

    Or is this a physics rule that is pretty much locked in place depending on the boiler's metal type and operating pressure?

    It doesn't seem to be that great a difference anyway
  • Arthur
    Arthur Member Posts: 216
    Pressure v temperature transfer.

    If the temperature is the same it makes on difference on a Low Pressure hot water system. You still run the boiler at the same temperature (80 deg cent or 180 deg fah) it is the temperature difference (delta T) which affects heat transfer not the pressure as per Steamhead said.
  • In most cases

    the difference is minimal where the static fill of the system is 12 psi or even 20. Where it does make a difference though is in elevated pressure hydronic systems where static fill may be much higher. Most commercial boilers now come equipped with 50 psi relief valves and are actually rated for 80 psi. In this case, the saturated temperatures within the boiler can approach 300°F. Introduce into this environment return water cooler than 130°F and you may have some thermal stresses going on within the boiler sections. This is why we and most other manufacturers advise and stress the use of either a properly sized blend pump, modulating three way diverter valve and a return sensor to divert or bypass heated supply water to the return side to always keep the return side warmer. Hope this helps.

    Glenn